I’m currently setting up a 2WB smoke detector on Zone 1 of a Vista 20P system. I believe I wired it correctly, but the detector triggers an alarm every 30 seconds. After silencing the alarm and resetting the power, the issue persists. There’s no visible smoke, but there might be dust due to ongoing construction. However, the sensor was installed today, so it hasn’t had time to accumulate dust.
Here’s how I’ve wired it: The wire from the panel (HI) is connected to the (+) on the left side. I placed a 2k resistor between the (+) on the right side and the (-). The wire from the (-) is connected to the panel (LO). There’s only one smoke detector on this loop.
One thing to note is that there’s a sizable hole where the wire exits the ceiling and connects to the detector, and there’s some draft coming through. Could this draft be causing the false alarms?
Any guidance on this would be greatly appreciated!